just a quick question. im installing 10 x 4 foot fluorescent fittings, each with 4 x 36w tubes.
I was under the impression that each fitting would use 144watts, so all 10 would be 1440watts, which would be 6.2 amps in total.
The problem is it keeps tripping a 10 amp breaker and when ive had a clamp meter on the cable it says its pulling 11 amps.
Theres no more lights on the circuit, am i calculating something wrong?
 
it popping after about 5 mins. does the 1.8 factor just apply for the initial start up?

The 1440W figure is the real power but the apparent power (VA) is higher because there is a power factor associated with lamps because they are an inductive load. This is giving the 11A+ figure that you are seeing on your clamp meter. This will be there the whole time and cabling and volt drop should be calculated on the apparent power. As Lenny said multiplying watts by 1.8 is usually accurate enough. However your 10A mcb should not be unduly troubled by 11A for 5 mins so the tripping is probably down to a combination of the inrush / startup current and the overload. The peak inrush for the ballasts should be in the manufacturers specs. Inrush can be countered by using a C type breaker ( if the max Zs is ok) but that still doesn't solve your overload. I reckon you probs need 2 circuits both on 10A mcbs :)
 
Last edited by a moderator:
The 1440W figure is the real power but the apparent power (VA) is higher because there is a power factor associated with lamps because they are an inductive load. This is giving the 11A+ figure that you are seeing on your clamp meter. This will be there the whole time and cabling and volt drop should be calculated on the apparent power. As Lenny said multiplying watts by 1.8 is usually accurate enough. However your 10A mcb should not be unduly troubled by 11A for 5 mins so the tripping is probably down to a combination of the inrush / startup current and the overload. The peak inrush for the ballasts should be in the manufacturers specs. Inrush can be countered by using a C type breaker ( if the max Zs is ok) but that still doesn't solve your overload. I reckon you probs need 2 circuits both on 10A mcbs :)

Good answer mate.
 
one more thing, anyone know any good books regarding the design side?
You could try this one - probably the best for electricians and associated trades

Electrical Installation Design Guide: Calculations for Electricians and Designers - IET Electrical

I hope I'm not infringing any advertizing on the forum :nonod:
 
one more thing, anyone know any good books regarding the design side?

If it is a case of you knew it once and have forgotten then the IET's electrical installation design guide is ok and it has some examples, but it does go into a lot of detail and you might find it heavy going. If you are more of a beginner then On Site Guide is a good a place to start as anywhere. (appendix F in the new one)
 

Reply to quick calc question in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

  • Question
Hi tssxrr, I am also doing my assignment on the same topics. would you mind sharing the documents which you have done so I will have rough idea...
Replies
1
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top