Went to a job last week. No cooker feed to a new kitchen that been fitted this week. Customer thought they could use the socket that the old oven used. (old hob was gas) anyways i ran a 6mm to the kitchen and 6mm tail for the hob to connect to as the customer didnt know the rating etc and just said it would be a normal cheap ish cooker.
Been back today and the hob is noraml as she said but the instructions say 2.5mm to the terminals on the hob ??????? no way will the 6mm twin i put in fit in the terminals its just too damn big.
Am i right thinking that the manaul is onabout using 2.5mm Flex and not twin. How do i go on with the 6mm feed i put in for the supply and the 6mm s/w to the hob.
Looked in the onsite guide at diversity and i get the following.
10A + 30% of the remaining + 5A if there is a socket (there is) outlet on the switch.
Hob is 6200watts
6200/240 = 25.83A
so i have 10A for a start + 30% of remaining 15.83A = 4.79A + 5A
total = 19.79A
Is this correct?
What size breaker would be best to use. Wouldnt it trip with a 20A ?
Bit lost here guys... thanks
Been back today and the hob is noraml as she said but the instructions say 2.5mm to the terminals on the hob ??????? no way will the 6mm twin i put in fit in the terminals its just too damn big.
Am i right thinking that the manaul is onabout using 2.5mm Flex and not twin. How do i go on with the 6mm feed i put in for the supply and the 6mm s/w to the hob.
Looked in the onsite guide at diversity and i get the following.
10A + 30% of the remaining + 5A if there is a socket (there is) outlet on the switch.
Hob is 6200watts
6200/240 = 25.83A
so i have 10A for a start + 30% of remaining 15.83A = 4.79A + 5A
total = 19.79A
Is this correct?
What size breaker would be best to use. Wouldnt it trip with a 20A ?
Bit lost here guys... thanks