Went to a job last week. No cooker feed to a new kitchen that been fitted this week. Customer thought they could use the socket that the old oven used. (old hob was gas) anyways i ran a 6mm to the kitchen and 6mm tail for the hob to connect to as the customer didnt know the rating etc and just said it would be a normal cheap ish cooker.

Been back today and the hob is noraml as she said but the instructions say 2.5mm to the terminals on the hob ??????? no way will the 6mm twin i put in fit in the terminals its just too damn big.

Am i right thinking that the manaul is onabout using 2.5mm Flex and not twin. How do i go on with the 6mm feed i put in for the supply and the 6mm s/w to the hob.

Looked in the onsite guide at diversity and i get the following.
10A + 30% of the remaining + 5A if there is a socket (there is) outlet on the switch.

Hob is 6200watts

6200/240 = 25.83A

so i have 10A for a start + 30% of remaining 15.83A = 4.79A + 5A

total = 19.79A

Is this correct?

What size breaker would be best to use. Wouldnt it trip with a 20A ?

Bit lost here guys... thanks
 
I too would use 2.5mm H07RN-F from the outlet plate to the hob. Make sure you use either cord end terminals or ring crimp terminals and not just put the flex under screw heads.
A 32A MCB will be fine.
 
Your calcs seem Ok I use 230v in mine but the difference is negligible , The current rating you've found seems fine for the HO7 its got a bit tougher rubber sheath so it wears better where abrasion is likely and it's heat resistant which gives it the higher current carrying capacity than the normal flex.
 
Last edited by a moderator:
I would use 4mm H07RN-F if it will fit in the terminals, but when the destructions say to use 2.5mm this is usually code for "don't even bother with 4mm cos it won't fit mate". The manufacturers use small terminals to save on costs.

Yes, discrimination can be applied to hobs. I get 15A, 20A with a socket.
 

Reply to Quick Cooker Question in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
943

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
689
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top