If you did a PIR for a 2391 exam and after testing found insulation resistance on a circuit to be 0.4M Ohms between line and earth on an outside light which code would you use?
Would you use code 2, requires improvement or code 3 requires further investigation?
I used code 3 and got the wrong answer according to this mock test I am doing.


Also if you found the breaking capacity of the fuses to be below the PFC would you code 1 or code 2 it?

Thanks alot.
 
Last edited:
the first part could be a 2 or a 3 IMO. the second part i would code 2. as requires improvement, but no immediate danger.
 
The other codes were to do with not having RCD protection in the offices, Code 4.
Now I thought offices were full of skilled and instructed persons.
I guess if the question does not mention they are skilled and instructed then you have to assume that they are not.
Also the work shop ring had no RCD protection code 4.
I thought work shops were full of skilled and instructed persons and the only time you would need RCD protection was if you had a socket that could be used for mobile equipment outdoors.
I wonder how flexible City and Guilds are with their answers to coding questions.
 
Last edited:
That IR question is a little teaser. If you read Reg 612.3.2 it states

" The insulation resistance measured with the test voltages indicated in Table 61 shall be considered Satisfactory if the main switchboard and each distribution circuit tested separately, with all it's final circuits connected but with current-using equipment disconnected, has an insulation resistance not less than the appropriate value given in Table 61"

So as your reading was 0.4 Mohm it can not be seen as satisfactory and yes a code 2.
 
Last edited:
Zs reading above max. allowed. boxed in BS951 clamp on water or gas so you can't actually see that it's connected. anything that you think requires further investigation to determine if it's satisfactory or not.
 
Tough one, I read it out the book and am not sure myself.

I guess if he is in the car park testing an outside light and notices the car park lights that are not part of the inspection are falling apart with wires hanging out of them all over the place.
 
"The person ordering the report should be advised that the inspection has revealed an apparent deficiency which could not, due to the agreed extent or limitations, be fully investigated"
 
Absence of a main protective bonding connection to a lightning protection system where it is not known by the inspector if it is required to protect against lightning side flashes"
 
Absence of a main protective bonding connection to a lightning protection system where it is not known by the inspector if it is required to protect against lightning side flashes"

There you go there is another, which I would imagine is used quite a lot in down town suburbia.

These sort of examples are rare and that is why I think code 3 was rarely used, and is now being consigned to regs bin of history
 

Reply to Quick couple of coding questions in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
There is one reason to have an inspection every three years instead of the five. Itā€™s more work and money for them šŸ˜šŸ˜
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top