Just need convincing that I am still doing it right!
So,
16mm SWA, 50M run, 12Kw load 3P/N supply. (17.3A per phase)
16mm R1 + R2 = 1.15mOhms/Meter = 100x1.15/1000 = 0.115
ZS = 0.21 + 0.115 = 0.325
230/0.325 = 707A (fault current)
√ 707 x 707 x 0.1
---------------------
115 = 20.8mm?
Thanks