I have just been asked a question by a friend of mine and am not sure of the answer.

He has done a PFC test and found it to be 8.5 KA.

The main fuse is rated at 33KA but the MCB's (60898) are rated 6KA.

He has asked me if it will be compliant as the main fuse is rated higher than the PFC but I am not sure.

Can anyone help me with this one?

Thanks.
 
I guess he measured at the incoming side of the main switch.

I will send him a text and ask some more questions.

Would it be prudent to measure at the outgoing side of each MCB just to see what the figures are?

If the PFC is greater than 6KA at the outgoing side of the MCB then he will be in trouble right???
 
An extract from BS EN 60439-3.


"Part 3 of the Standard, BS EN 60439-3, deals with the particular
requirements for low voltage switchgear and control gear

assemblies intended to be installed in places where unskilled
persons have access to their use. This covers the supplementary
requirements for enclosure distribution boards suitable for indoor
use containing protective devices intended for use either in
domestic applications or other locations where unskilled persons
have access. Control and/or signalling devices may also be
included.
These distribution assemblies are for use on AC supplies, with a
nominal voltage to earth not exceeding 300V. The outgoing
circuits include short circuit protective devices, each having a
rated current not exceeding 125A with a total incoming load
current not exceeding 250A.
In the UK, such equipment is referred to as a ‘Consumer Unit’
and as such is covered by this Standard. However, additional
requirements from annex ZA of the standard call for the
assembly to have an additional test; this is known as the
‘conditional withstand test’. The condition is that the consumer
unit must withstand a 16kA short circuit fault when protected by
a 100A HRC fuse to BS 1361 type II. Further requirements are
addressed by this annex:
Means of isolation to be via a manual double pole switch
disconnector
Rated current of consumer unit is determined by current
rating of incoming device.
Outgoing protective devices can be MCB’s, Fuses and/or
RCBO’s."
 
So the boards and also the MCB's are tested to 16KA right?

The problem seems also that if there is a short circuit line to neutral fault the MCB might be damaged and need replacing.

Testing these boards to 16KA, are they still usable afterwards or do the MCB's need replacing?

A lot of questions but thanks for the help.
 
Last edited:
This product test is destructive in nature. The manufacturer's test at 16kA exceeds the MCBs Icn "one-time" fault current rating, often resulting in major damage to the DB, cabling and occasionally MCBs explode. However, the fault current must be interrupted in any unit that passes the test and therefore meets the standard.
 
So the boards and also the MCB's are tested to 16KA right?

If its a consumer unit along with protective devices complying to BSEN 60439-3 and the manufactures are utilizing the conditional short circuit test in Annex ZA of that standard then yes.

The problem seems also that if there is a short circuit line to neutral fault the MCB might be damaged and need replacing.

Possibly, it all depends on what the level of fault, PFC can be greatly reduced along the out going circuits.

Testing these boards to 16KA, are they still usable afterwards or do the MCB's need replacing?

If an MCB rated at 6kA is exposed to a current of 16kA Then it will need to be replaced, bear in mind at 16kA the 100amp Fuse will limit the current to around 9kA, even so the mcb would require replacement.

A lot of questions but thanks for the help.


Regards
Chris
 

Reply to Quick PFC question. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
846
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
968

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
667

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top