Hi, help required.
Control panel with a 125A 60947-3 main isolator feeding internal 16mm singles cable to a 80A M.C.B believed to have been originally 100A rated, a previous electrician removed this and down rated to 80A. This then in turn supplys internal control gear ( contactors, relays etc etc. )
The problem
The temp in the panel is 60 degrees plus i measured the 16mm singles between 66 and 67 degree celsius. Maximum demand has not been established but should not exceed 100A.
Am i safe to say that in this situation according to cable ratings they are rated at 67A? if so would i be correct in saying that if i were to swap with 25mm or 35mm singles then also revert back to a 100A M.C.B this would be problem solved? I have suggested that the temperature needs to be reduced so as not to add to the problem.
Thanks Kev
Control panel with a 125A 60947-3 main isolator feeding internal 16mm singles cable to a 80A M.C.B believed to have been originally 100A rated, a previous electrician removed this and down rated to 80A. This then in turn supplys internal control gear ( contactors, relays etc etc. )
The problem
The temp in the panel is 60 degrees plus i measured the 16mm singles between 66 and 67 degree celsius. Maximum demand has not been established but should not exceed 100A.
Am i safe to say that in this situation according to cable ratings they are rated at 67A? if so would i be correct in saying that if i were to swap with 25mm or 35mm singles then also revert back to a 100A M.C.B this would be problem solved? I have suggested that the temperature needs to be reduced so as not to add to the problem.