Quick question that come up in college | on ElectriciansForums
Discuss Quick question that come up in college in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
A
AshFR
Hi all. Just a quick question that come up in college. Why is the r1+r2 values lower than the Zs on the same circuit?
Example: Cooker Circuit - R1+R2 = 0.4ohm, Zs = 0.6ohm
Why is the Zs higher than the R1+R2?#
Thanks.
Z stands for impedance.
Ze is the impedance external to the installation.
Zs is the total impedance from source, up to the point of measurement.
As such Ze is measured at the origin of the installation, Zs is measured along whichever circuit you are testing, and the highest reading is recorded as being Zs for that circuit.
It should be noted, that Ze is measured with parallel earth paths such as Protective Bonding Conductors disconnected.
Ok well looking at some test results from a few years back, it says Ze at origin is 0.13ohm and cooker circuit r1+r2 = 0.4ohm and Zs = 0.6ohm
How did they get Zs at 0.6ohm when r1+r2 (0.4) + ze (0.16) is 0.56?
you will get some effect from parallel paths that will give a lower Zs than expected. but also the internal components of MCBs etc. may give you a higher value.
Awesome. Thank you very much. Really need to freshen up on my inspecting and testing as i hoping ive got my AM2 in a few months.
Every joint or connection can introduce a resistance.
Also there is a slight difference between resistance and impedance, with impedance being slightly higher than resistance, as impedance involves both resistance, and reactance (capacitive and inductive).
Dude, get your head in your books and get learning. You should really know if you are approaching the AM2 exam what the formulae Zs=(R1+R2) + Ze stands for.
Reply to Quick question that come up in college in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
OLDBOY
O
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...