Hi there, I was wondering might anyone be able to answer a few of these questions that I cant find an answer:
- Firstly with switch start fluorescents do I use the 1.8 correcting factor when calculating the total load? Why is this?
- does the correction factor apply for digital ballasts as well?
- Does this correcting factor also apply for any other type of fitting such as SON / Metal Halide?

cheers
 
discharge lighting is highly inductive and even though the lamps are rated in watts the whole unit should have a VA rating.
its this VA rating that the current is calculated.
if no VA rating is given then a value of 1.8 is used to calculate it from the wattage. so its watt x 1.8 = VA.
circuits can then be calculated from this
 
Last edited by a moderator:
Final circuits for discharge lighting must be capable of carrying the total steady state current, i.e. lamp current plus any associated control-gear current including their harmonic currents.
Where more accurate information is not available, the demand in VA is taken as the rated lamp W multiplied by =>1.8. The 1.8 multiplier assumes a power factor of not less than 0.85 lagging and takes account of the control-gear losses and harmonic current.
 

Reply to Quick question in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

  • Question
This potential client seems to be making progress in terms of being interested in proper chargers and answering my query questions. I have also...
Replies
13
Views
2K
  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
665

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top