new to this so just looking for a bit advice and to see your thoughts had a quick test on a garage todayjust to check condition of wiring results i got were.

Tnc-s supply 6mm armour out to feed main board in garage

sockets zs- 0.56
R1-0.32
rn-0.32
R2-0.48
R1+R2-0.48

Insulation
L-N 82.6M
L-E 70.6M
N-E 0M

now my questions i thought R1,R2 was meant to be a quarter of R1+R2?
on the insulation test did i get a dead short due to earth and neutral having the same potential?
any help would be great
 
now my questions i thought R1,R2 was meant to be a quarter of R1+R2?
on the insulation test did i get a dead short due to earth and neutral having the same potential?
any help would be great

R1 + R2 = (r1 + r2) / 4.

As for insulation resistance, how do you know it's a dead short?

0 million ohms isn't necessarily the same thing as 0 ohms.
 
thanks for the reply so saying that R1+R2 should be 0.2 going with my results am i correct there?

as for the insulation i just tested N-E at 250v and it said 0.00 M ohms thanks again in advance
 
yep, R1+ R2 should be 0.2 and as for the insulation resistance, i would imagine there is a short, probably a socket pin through the neutral, is it not RCD protected?
 
hi its tn-s in the house, no the cables were not discotted at the garage cu:eek: didnt realise you had to do that, what are your thoughts on the R1+R2 thanks again
 
If you tested the distribution board/installation as a whole then you need to disconnect the neutral/earth link for a TN system. Low Voltage systems should be tested at 500V d.c. (ELV 250V d.c.)

Yes, I make it 0.2 ohms as an expected approximate value for R1+R2.
 
R1-0.32
rn-0.32
R2-0.48
R1+R2-0.48

now my questions i thought R1,R2 was meant to be a quarter of R1+R2?
on the insulation test did i get a dead short due to earth and neutral having the same potential?
any help would be great

Well the calculation on a ring would work out at (r1+r2)/4, but if you have done the figure of 8 test then this could have been due to spurs. If the figure of 8 test was conducted the other way around, you could get spurious results.

The live neutral fault could be due to the main switch not being open. If this is the case, then you would be seeing the neutral-earth link the PME head if it's TN-C-S, or back at the star point of the transformer if it's TN-S.

Make sure you've isolated from the main switch, and left all MCB's on and fuses in place.... :)
 
Well the calculation on a ring would work out at (r1+r2)/4, but if you have done the figure of 8 test then this could have been due to spurs. If the figure of 8 test was conducted the other way around, you could get spurious results.

The live neutral fault could be due to the main switch not being open. If this is the case, then you would be seeing the neutral-earth link the PME head if it's TN-C-S, or back at the star point of the transformer if it's TN-S.

Make sure you've isolated from the main switch, and left all MCB's on and fuses in place.... :)

for anyone like me who didnt know what spurious was:eek:

–adjective1.not genuine, authentic, or true; not from the claimed, pretended, or proper source; counterfeit.
 

Reply to quick test on a garage in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
996
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top