.r.c.d. Ramp test

U

underpar12

HELLO
on way to job tomorrow to ramp test a 30ma r.c.d,would i be right in saying any reading below 15 ma is unsatisfactory and over 15ma is satisfactory.many thanks :confused::rolleyes:
 
thanks for your replies , do i ramp test with all loads /m,c,b,s in the off postion twice ,then with m,c,b,s on to see if any earth lekage is present .
 
Idealy 25 - 29mA would be the optimum figure, although any figure above 15mA and below 30mA the RCD will be within limits.


Sent from my iPhone using Tapatalk.
 
HELLO
on way to job tomorrow to ramp test a 30ma r.c.d,would i be right in saying any reading below 15 ma is unsatisfactory and over 15ma is satisfactory.many thanks :confused::rolleyes:

That would indicate that it would trip at x 1/2, which is unacceptable. Anywhere < 23-24mA would suggest replacement for me.
 
As long as it doesn't operate at half the rated residual operating current and does operate within (assuming BS EN 61008/61009 device) 300mS at rated residual operating current then it meets the requirements. Plenty of devices operate below 25mA - nothing faulty about them though.
 