HI JUST INSTALLED A 12 way dual r.c.d. consumer unit.
problem is on the lighting circuits . at present i have both upstairs and downstairs and smoke alarm ,s on separate circuits,had to disconnect all three circuits to keep both r.c.d.s from tripping.out of intrest i tried all three circuits in a r.c.b.o on the non r.c.d. side but as soon as one of the circuits c.p.c our reinstated to the earth bar it trips out, started to check fittings etc seen that the smoke alarms have used the c.p.c as a interconnection. i am thinking also that some one has also linked both circuits together. so to recap as soon as one of the c p.c. is installed the r.c.b.o.s trip . any suggestions.
problem is on the lighting circuits . at present i have both upstairs and downstairs and smoke alarm ,s on separate circuits,had to disconnect all three circuits to keep both r.c.d.s from tripping.out of intrest i tried all three circuits in a r.c.b.o on the non r.c.d. side but as soon as one of the circuits c.p.c our reinstated to the earth bar it trips out, started to check fittings etc seen that the smoke alarms have used the c.p.c as a interconnection. i am thinking also that some one has also linked both circuits together. so to recap as soon as one of the c p.c. is installed the r.c.b.o.s trip . any suggestions.