R1 and R2 Maximum value
Am I right in thinking that for any ring circuit the maximum value that r1+r2 can be is 1/2 the loop reading on the phase + 1/2 the loop reading for the cpc ( measured at the CU ) Or has my maths let be down?
the r1 r2 for a ring should be live-live + cpc-cpc devided by 4
so you are on the right lines your terminoligy is a bit out
ideal reading not max
continuity not loop
(R1+R2) = (Line loop plus cpc loop)/4.
Doesn't matter what csa cpc is in relation to Line conductor as you are adding the two and dividing the lot by four.
In a ring final circuit you are effectively halving the length of the conductors and doubling the cross-sectional area.
Of course it matters......Will the end to end readings not be different for a ring circuit with a 1.5mm cpc and a 2.5mm cpc.
In a 2.5/1.5 ring the yardstick is 1.67 times the the line/neutral end to end value for the cpc.
hey len
yeah the end to end readings will vary depending on the ratio of the cpc size
but its still r1+r2 divided by 4
.20r1 + .34r2 /4 = .08 (2.5/1.5)
.20r1 + .20r2 /4 = .10 (2.5/2.5)
i suspect we all know what we mean but its getting lost in "translation";)
But what if the ring is wired in 4mm T& E or 4mm singles?
As Mr Mark Sparks says it is ALWAYS (R1+R2) = (r1+r2)/4 for a ring final circuit. As I say, it makes no difference what csa the cpc is as the equation is still dividing the total of your end-to-end loops by four.
The max R1+R2 for a ring final circuit is the maximum value measured during step 3 of the 3 step test. See OSG page 80 - 10.3.2 The formula quoted by others (r1+r2)/4 is only correct for sockets wired on the ring. Spurs will show a higher reading hence the need for the 3 step test to identify spurs and to confirm the ring is correctly wired.
IMO the (r1+r2)/4 is only a guide as to what you should get for R1+R2. same as for example if you had a circuit of 10m 2.5/1.5, you would expect R1+R2 to be around 0.2ohms, using the resistvity table 9A OSG. the values entered on a certificate must be measured values.
Golden_Boy,
telectrix,