Can anyone help me, I've been asked to do an inspection on a property that is on a single 32A ring, including the kitchen. The appliances are all integrated and aren't spurs. Is there a way to perform the test with these appliances in place?

Thanks!
 
No they are wedged in. It's a posh kitchen and the owners don't want me pulling their integrated appliances out. Someone was telling me I could do a combined N/L to CPC test instead but I don't know if this would work or is even compliant to regs.
 
As long as its noted on the report that the appliances can not be unplugged then you need to IR test L-N to CPC on that ring. Just note it as a limitation, but if you can't get to sockets then I think that in it's self may warrant a code.
 
Ok thanks a lot. What can I do regarding the R1&R2 test as there are loads on the ring, will this not throw my readings out?
 
Your R2 maybe higher due to the earth on the appliances

Do your end to end and see if your R2 is alot higher than the normal 1.67x, you probably find there's not much in it
 
Last edited by a moderator:
most appliances have double pole switches, so, as long as they are switched off, they should not affect your readings. R1+R2 should read (r1+r2)/4. fridges and freezers though could be a problem, as they don't have an ON/OFF switch.
 
Unless the socket that the appliance is plugged into is a spur off the ring then the R1+R2 will be higher than the calculated method. The fact there is no method of isolating each appliance without the use of a tool (Removing integrated appliances) would be a concern to me.

As tel says be sure the appliances are in the off position, on the ones that can, I'd also do IR at 250v first to see if there is any load affecting those readings, if not then your safe to go up to 500v
 

Reply to R1&R2 and Insulation Resistance Test with fixed appliances in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
924

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top