ive just tested a 16a radial socket circuit. r1+r2 was 0.14 ze was 0.2 but measured zs was 0.74. am i right in thinking this is to high? why would i get this figure?
 
sound connections through out,even with bonding/parralell paths involved the reading should only be 0.16 or slighty more?
 
I take it you did the Zs using plug top method at last point at radial ? Check connections at board and back of socket(s) or measure it with probes on the back of socket see if the same (Don't forget your safety specs)..
0h and was this a hard test or a soft test ?
 
Last edited:
yes measured zs with plug adaptor, what reading would you be looking for steve? also why will ze=r1+r2 never really give an accurate reading? thanks for all your help im quite new to the testing side of things and classroom learning and on the job situations are a bit different!!
 
reading is well below max. allowed for 32A MCB. acceptable. if you test on no trip for Zs and high current for Ze, that could be the reason. still poss poor connection. terminal screw thru insulation? try other sockets. if you get big difference between 2 sockets, that,s where to look for bad connection
 
Last edited:
no its a 6m run clipped to joists under floor,no insulation anywhere near it, im going to go back and retest it as its playing on my mind now and i want to sleep tonight!
 
I wouldn't worry about this at all, u will never get a calculated answer bang on when u use your megger, especially if it's on no trip, u can be up to 2.87 ohms on a 16 amp mcb so u have a good reading, also just make sure u zero ur leads out?
 
cheers lads, im planning on using it for an niceic assessment so probably being a bit over cautious,as i say megger is brand new so perhaps it is the no trip/high settings. ill have a play with it tommorow on another installation and see where i go. thanks again
 

Reply to r1/r2 and ze dont measure up? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
251
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
998

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top