I have measured the highest R1+R2 on a lighting circuit as 1.51 ohms at a switch. However, I get 0.86 ohms on a ZS test at the same point. I am on TNCS system and my Ze is 0.22 ohms. Although I expected a lower ZS by measurement than by calculation, I did not expect it to be this low. I understand parallel paths will lower it but by this much?

Views please.

Thanks PP
 
estimate the cable length. that 1.51ohms for 1.0/1.0mm would indicate a cable run of 40m. if it's 1.5/1.0mm, even longer ( i don't have the figure to hand). seems a bit high.

edit: 1.5/1.0mm a res. of R1+R2 of 1.51ohms would indicate a circuit length of approx 60m.
 
Last edited:
Its 1.5/1.0 and it is no way near 40m. It is an unusual reading compared to the others around the place. I would say 10m tops. Loose connections somewhere?

EDIT: Even so, why the much lower ZS with the 1.51 ohms R1+R2?

Thanks PP
 
Last edited by a moderator:
think its your R1+R2 is out. 10m should be 0.3ohms. leads not nulled properly or a high resistance connection, not seen on the Zs test.
 
Last edited:
When I tested R1+R2 by removing the conductors from the switch, I still got 1.51 ohms, ish. I don't understand why bad contacts are "not seen" when a ZS test is done either tbh.
 
maybe the fact that the Zs test is a live test with 230v on the circuit. continuity testing is done at 12v or less.
 
remember that on a 2 way curcuit, your R1+R2 is through 2 closed switches. this could be as wp says. also, it's common for the 3core between the switches to me 1.0mm, not 1.5mm.
 
There must be something up with the switch drop. I had about 0.68 ohms at the light point on a two way circuit. Mmm

Excellent point. I will try testing without switches and see what I get. Mind you, the ZS is fine and that's the main thing I suppose.
 
Last edited by a moderator:
what you could do is link out the switches and read again for R1+R2. if the reading drops, then you've proved it.
 

Reply to R1+R2 and ZS results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
919

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
254
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top