No you cannot.

You need to measure R1&R2 to verify both polarity and the presence of conductors before energising the supply.
Also, a measured Zs test will incorporate parallel paths which will more than likely indicate an inaccurate R1&R2 if obtained by calculation.
 
Is it alright to take away ze from zs to get r1 + r2 reading

No indeed.

A measured Zs value will include any additional parallel earth paths that may be present in the installation......protective bonding for instance, so the Zs-Ze will not be a true reflection of the resistance of the line & CPC conductors of the circuit in question.
 
but is it necessary on a PIR to measure R1+R2, as the circuit has already been verified when installed and energised. measurement of Zs, when compared to previous readings should confirm that the R1+R2 is satisfactory.
 
but is it necessary on a PIR to measure R1+R2, as the circuit has already been verified when installed and energised. measurement of Zs, when compared to previous readings should confirm that the R1+R2 is satisfactory.

Well if you didn't then how would be able to test polarity (things like switching of the Line conductor only), or things like open circuits on ring finals and bridges within them?
 
Well if you didn't then how would be able to test polarity (things like switching of the Line conductor only), or things like open circuits on ring finals and bridges within them?

live polarity with ZS
open circuits ? do you mean one conductor disconected making a big radial?
well by comparing the ZS from previous PIR
 

Reply to r1 + r2 by taking away ze from zs in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top