O

ohthatshowyoudo

ANY HELP ON THIS LADS APPRECIATED!!
ok haveing tested a 230v 50hz circuit 100mtrs protected by (mcb 16a type c max ZS 1.44) (20a contactor) feeding (4 x 400w sodium floods)... the readings were as follows ..(cpc r1+r2 = 1.47ohms) Ir=>1999 (Ze = 0.01ohms) pfc 6.00 ka/ are my calculations correct in checking shock risk.... Zs = Ze+r1+r2=ohms so Zs= 0.01 + 1.47 = 1.48ohms over so fails..
i also wanted to check the design calculation for this circuit and my mind is frazzeld as to what table and page in regs i can find the r1 + r2 milohms/per mtr calcs for 6mm swa

any help plz :confused:
 
Hi sorry about the confussion but yes these were the readings i took and i should have noted the if = Uo-ze was not correct i have just started testing so was puzzled by these results. and wanted to start from scratch and calculate the design from installed equipment. i will be doing another earth loop at at distribution. and yes i am able to take Zs at end of circuit but wanted to get full understanding of readings i have so far... again sorry for my lack of knowledge but i am new to this game and would like help.
 
Hi jemma jones
i will be looking at testing circuit again and getting new results. but please can you advice on the correct calculation for compliance and correct table for the shock risk so i can do design calculation from chair..... then when i have correct confirmed results i can cross referance these results.. at the moment i am in the dark the installation has been designed and they have not provided any test results or schematics. i am just struggling finding the r1 + r2 values for 6mm swa and the temp values for correction
 

Reply to r1 + r2 calculations in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top