ok haveing tested a 230v 50hz circuit 100mtrs protected by (mcb 16a type c max ZS 1.44) (20a contactor) feeding (4 x 400w sodium floods)... the readings were as follows ..(cpc r1+r2 = 1.47ohms) Ir=>1999 (Ze = 0.01ohms) pfc 6.00 ka/ are my calculations correct in checking shock risk.... Zs = Ze+r1+r2=ohms so Zs= 0.01 + 1.47 = 1.48ohms over so fails..
i also wanted to check the design calculation for this circuit and my mind is frazzeld as to what table and page in regs i can find the r1 + r2 milohms/per mtr calcs for 6mm swa
any help plz
ok haveing tested a 230v 50hz circuit 100mtrs protected by (mcb 16a type c max ZS 1.44) (20a contactor) feeding (4 x 400w sodium floods)... the readings were as follows ..(cpc r1+r2 = 1.47ohms) Ir=>1999 (Ze = 0.01ohms) pfc 6.00 ka/ are my calculations correct in checking shock risk.... Zs = Ze+r1+r2=ohms so Zs= 0.01 + 1.47 = 1.48ohms over so fails..