armbands0

Completed a small job PIR carriage lights, on a garage, controlled by a standard light switch inside the garage. Testing R1+R2 the result seemed high, approx 6M of 1.5 t&e (1.24R).

I know you be screeming, it were the switch contacts, as I am a newbie it took me a while longer to sus the dodgy switch. Excersied it a few times and the reading was as expected.

Replaced the switch with an MK, no more budget switches for me.
 
MK oh yes they are good as ever , did you zero your leads befor testing , the high reading could be due to a loose connection , an r1 r2 reading on 1.5mm twe oer 6 meters i would expect to be less than 0.20 ohms
 

Reply to R1+R2 dissapointment. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top