Hoping someone can shed some light on why, when i tested R1+R2 on the double sockets on a ring in my garage, on 1 side of the socket i got a reading of 0.25 ohms (which was consistant with other sockets on the ring ) but on the other side i got 0.46 ohms ?? They are old socket faces (approx 6 years) checked all terminations which are fine, not sure why i would get this reading?? Any takers?
 
try shoving a plug in and out a few times. could also be resistance in the switch. flick it on and off a few times.
 
Last edited:
had the same problem during my 2391 the examiner mentioned what tele and tony said about the resistance of the socket outlet especially old ones, but this does greatly affect the resistance and the 0.05 difference allowance goes out the window unless you remove each socket on the ring and test, but my boss works it out on 20min a circuit not too great when you get a board full of rings !!
 
had the same problem during my 2391 the examiner mentioned what tele and tony said about the resistance of the socket outlet especially old ones, but this does greatly affect the resistance and the 0.05 difference allowance goes out the window unless you remove each socket on the ring and test, but my boss works it out on 20min a circuit not too great when you get a board full of rings !!
When i was doing my 2391 i was told that the 0.05 allowance was only for the loop conductors when tested at the DB and not on the socket .
 
I would consider it a defect unless there were visible signs of corrosion. You should find that the Zs value is more of an indication if there's a problem with the socket outlet. If it produces an excessive resistance, then recommend a change.
 
When i was doing my 2391 i was told that the 0.05 allowance was only for the loop conductors when tested at the DB and not on the socket .

the 0.05 allowance is for the end to end tests at the DB on all conductors of the ring unless its T&E where youd expect 1.67 times higher compared to line and neutral

and on step 2 and 3 the 0.05 still applies because you are testing the same length of circuit at each point, these readings are the readings for R1+R2 on the line and cpc figure of 8 test, the figure of 8 tests that the ring hasnt been installed wrong by being bridged etc
 
the 0.05 allowance is for the end to end tests at the DB on all conductors of the ring unless its T&E where youd expect 1.67 times higher compared to line and neutral

and on step 2 and 3 the 0.05 still applies because you are testing the same length of circuit at each point, these readings are the readings for R1+R2 on the line and cpc figure of 8 test, the figure of 8 tests that the ring hasnt been installed wrong by being bridged etc
I agree with you ,but that is in ideal world when every thing is new and properly connected ,in the real world the resistance measured on the socket outlet can be different because of mechanical part of the socket itself , specially the were and tear during the life of the socket.
 
I agree with you ,but that is in ideal world when every thing is new and properly connected ,in the real world the resistance measured on the socket outlet can be different because of mechanical part of the socket itself , specially the were and tear during the life of the socket.

yeah definately aslong as the readings are about the same i think its acceptable i know a lot of sparks who dont even do the three step method and probably dont remember how they just end to end test them and R1+R2/4 and put down the expected reading rather than the measured one
 

Reply to R1 + R2 doubled on the double in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
832
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
930

Similar threads

It's a room where someone sleeps, so it's a bedroom. Minimum standards were set in the Parker Morris report in around 1963. Anything built after...
Replies
5
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top