Discuss R1 + R2 Lamps removed? in the Australia area at ElectriciansForums.net
That is though lads if you find the right earth that goes with the right Line ................not always easy in a 32 way TP+N+E DB.
On an initial verification you would do your R1 + R2 before you connected to the board, but on a PIR it may be a little different.
Along the TP+N+E DB lines, I have a PIR ongoing with 80-100 high bay lights in a warehouse to test. Wondering how many ccts fittings to test etc
ps should I post a new thread in ' Testing. Inspections'
Which is exactly why I don't bother with R1 + R2 on a PIR, just Zs.That is though lads if you find the right earth that goes with the right Line ................not always easy in a 32 way TP+N+E DB.
On an initial verification you would do your R1 + R2 before you connected to the board, but on a PIR it may be a little different.
It's not a limitation, as you are not required to record R1 + R2 on a PIR, just to confirm continuity and polarity of conductors.Spin - what do you document as a reason for the LIM in this case? Thanks.