Hi, does anyone remove lamps when testing R1 + R2 as it says in OSG & GN3.

I`m only getting a 0.02 ohm difference on a 4 light circuit.
 
Oooh, are you sure Jimmy?

Depends on how you're measuring it.
If you're putting a link between the earth bar and the protective device and measuring at the light you'll be picking up a parallel path through the lamp and Neutral to Earth/Neutral connection on a TNCS or all the way back to the supply transformer on TNS along the Neutral & Earth.

So you'll get a lower measurement.

Try drawing it.
 
Last edited by a moderator:
That is though lads if you find the right earth that goes with the right Line ................not always easy in a 32 way TP+N+E DB.

On an initial verification you would do your R1 + R2 before you connected to the board, but on a PIR it may be a little different.

Along the TP+N+E DB lines, I have a PIR ongoing with 80-100 high bay lights in a warehouse to test. Wondering how many ccts fittings to test etc

ps should I post a new thread in ' Testing. Inspections'
 
Along the TP+N+E DB lines, I have a PIR ongoing with 80-100 high bay lights in a warehouse to test. Wondering how many ccts fittings to test etc

ps should I post a new thread in ' Testing. Inspections'

There are a few factors to this

1 Age of Installation
2. Type of environment
3 Condition of the installation
4 Any previous testing done
5 If any previous testing done what was the results and when was it done.

Obviously a 5 yr old installation is likely not to need as much sampling as a 40 yr old installation that as never been tested, but inversely a poor 5 yr old installation may need more sampling that an excellent 40 yr old one, it is really you judgement and experience when doing a visual inspection at the beginning before you quote for the job.

In PIR work all the training and book study is really a poor second to experience as an experience electrician will within a few hours have a fairly good take on how much work and sampling is going to be needed.
 
Thanks Malcolm, I had my few hours assessing the general installation and decided that, in general, a vast majority of the db's (15 of) needed full test and inspection. It,s just a question of the lighting. The storage warehouse is an old 2nd world war munitions factory, no previous test details. It was used previously as some kind of engineering works, with db's added at over the years for various equipment added. Looking at the original lighting system, it is a joy to behold, obviously being designed to a very high spec, and takes me back to my apprenticeship days. However many of the lights are no longer in use or not operating, I would imagine, due to age. So it's a case of time, sorting out an old 10 way db and 30 gang switch system.
What a building though. More steel than the Forth bridge.
 
Another week testing. About 150 sq yds, so not massive but double the amount of re-enforcement. took a local builder a week to knock through the outer wall fitting a door. Loads of ccts no longer in use so just disconnecting to remove at source. A lot of damage to various isolators throughout due to dumb stacker truck drivers, etc. May be a point with bonding regarding an external liquid gas supply tank ,still to check. Quite a few damaged overhead crane busbars, all supplies to be removed bar one. That may be a problem.
 

Reply to R1 + R2 Lamps removed? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
667
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Hi, I'm installing a smart lighting system for ambient lighting in a "traditional" kitchen dinning room it's a big area. I want to be able to put...
Replies
0
Views
161

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top