My meter seems fine but when measuring r1+r2 the reading really seem to jump about from 0.31 up to 0.71 is this normal on sockets

Why do the readings jump about on a ring figure 8. Test

R1 end to end was 0.61 rn was same and r2 was about 1.66 x r1
 
please edit post so we know when you mean r1,r2 and R1,R2. so confusing, mate.

and the reason the readings vary is usually crap sockets.
 
Tested leads all seem fine, new batterys fitted, mk sockets r1, r2 rn are all fine just R1+R2 could the quality of the terminal block used to join at the board do this. As they are not the normal ones i use. Picked them up in trade point has hard white plastic coating and dont look brass or copper.
 
please edit post so we know when you mean r1,r2 and R1,R2. so confusing, mate.

and the reason the readings vary is usually crap sockets.

Sorry mate using my phone and.keyboard is rubbish lol and not sure how to edit this post but i mean big R1+R2 hope you can forgive me :)
 
that's what happens when you use something that'e designed for making phone calls as a typewriter. it's bad enough with these big keys.LOL.
 
drop socket and test straight from terminals, socket adaptors don't make good contact in worn sockets. from figures it looks like old 2.5t+e with 1mm cpc. probably some dodgy connections in there somewhere also.
 
Last edited by a moderator:

Reply to r1+r2 on ring figure 8 readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
919

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top