R1+ R2 reading | on ElectriciansForums
Discuss R1+ R2 reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
M
markb
I got a reading of R1+R2 for an outside twin socket of 0.06 ohms where i ran from c/u 2.5mm T+E to adapator box outside using 2.5 3 core swa just need to know if this reading is ok.(TNS)
The reason being is done the same on another house and the R1+R2 showed 0.31 ohms for socket.
It's more than Ok. Better than your last job. Why wouldn't it be O.K? Ensure you carry out an ELI also, and if it's a new circuit from the C/U it would require a domestic installation certificat. GOOD LUCK.
Reply to R1+ R2 reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.