Hello there,

i'm a bit new to this this is my first question on any forum, let alone the electricians forum.

When performing an r1 r2 on a ring main, and you can't identify one leg from the other, ie singles or the db is really congested.
How can you ensure you are connecting the correct earth to the live of the other leg, and vice versa.
Without having to pull the circuit apart.
Will you be able to tell by differing measurements.
Any help will be greatly appreciated.
John.
 
if its a ring, you will get end to end continuity L/L, N/N, E/E on the correct ends. always mark cables when installinjg, makes life a lot easier
 
Stage 1 = end to end test. Results will be r1, rn,r2
Stage 2 = Interconnect Line and Neutral. Test at all points. Results should be (r1+rn)/4 at each point, + or - 0.05ohms of your expected result.
Stage 3 = Interconnect Line and c.p.c. Test at all points. Results should be (r1+r2)/4 at each point, + or - 0.05ohms of your expected result.

If you see your readings rise slowly to the mid-point of the ring then drop again as you return to the DB then you've interconnected incorrectly.
If it's done right, you should recieve the same reading on all points of the ring as when they are interconnected correctly there is no mid-point of the ring.

Your on-site guide will give you a better explanation.
 
just a tip if you are really stuck identify the circuit and test it all from a socket with cables still connected at D.b readings should be the same.
 
some time ago, i knocked up an alarm internal siren wired into a pair of 4mm plugs (to fit breakout box). shove 12v from the CU down the correct L/N and you will hear it from anywhere in the building. on a ring you'l get 2 pairs that work
 
Last edited:

Reply to R1 r2, ring main. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
853
An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
656

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top