G

gpz900jim

When working on a ring main,Instead of working from a cu, which can be awfully crowded with wires, Would it be acceptable to take your r1, your r2 and rn readings and also cross connect your live and cpc in order to get your r1 plus r2 readings by taking a socket off and doing your work from there? Easier and safer ?
 
you have to measure end/end ( r1,r2,rN,) at the CU, but R1+R2 can be done by linking at the CU and measuring from sockets, no problem.
 
you can do it from a socket same results what if you are doing a large db with singles and cant turn everythin off and the conductors are not in right place on neutral bar or earth .
the only thing is you need to disconnect for insuletion resistance test because earth to neutral will give a short circuit result
but yes it is recomended for safety to test at socket if you ant switch of
 
on a old install taking a socket off is usually more trouble than doing it at the board, once you find how short the cables have been cut and the spur thats been added with cores all twisted together.
 
on a old install taking a socket off is usually more trouble than doing it at the board, once you find how short the cables have been cut and the spur thats been added with cores all twisted together.

This was exactly the thinking behind using the consumer unit for measuring ring final continuity and cross-connection tests.

At the consumer unit, you can see that all connections are in and tight before you 'lid up' you don't have that 'luxury' as you're pushing back an existing socket with conductors hardened from bending.
 
As you will know, it can be a real pain sometimes, when the wires have not been terminated in their correct places and the wires are jumbled together, and you are standing on a ladder, and its dark, and the cu cant be turned off..... Its useful to know that the ring can be tested from a socket. And its interesting to know that the nic recommend this method when a you have limited access
 

Reply to r1, r2, rn, r1 plus r2 ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
597
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
933
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
787

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top