Hi all Im new to this site so bare with me if im in the wrong place, Your help would be very much appreciated,
I have a ring main in a house and im testing r1 r2 rn,
I get 0.48 ohms on r1 0.48 ohms on rn but also get 0.48 ohms on earths, which is wrong as it should be 1.67 times that of r1 and rn i have been round every socket and all connections are tight,
it is 2.5 twin and earth with 1.5 earth wire not 1.0 earth wire,
Thanks
 
Wouldnt worry about it prob Supp bond, heating etc creating a par path - providing ir and zs is ok

If it had a 1mm cpc readings would be 2.5 greater not 1.67 although im sure you already know this
 
Last edited by a moderator:

Reply to r1 r2 rn ring test problems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top