r1 r2 testing on micc cable | on ElectriciansForums
Discuss r1 r2 testing on micc cable in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
stylus
Cumbria
when testing micc,pyro cable for r1 r2 values is it correct to use sheath as the r2 for a 2 core ?
Yes. thats fine.
These are the sheath CSA's that you will need to note on the test form......
Physical cross sectional area of MICC/PYRO copper sheath for use as CPC.
2L1 ****** 5.4 mm2
3L1 ****** 6.7mm2
2L1.5 ****** 6.3 mm2
3L1.5 ****** 7.8 mm2
4L1.5 ****** 9.1 mm2
2H1.5 ****** 11 mm2
3H1.5 ****** 12 mm2
4H1.5 ****** 14 mm2
2L2.5 ****** 8.2 mm2
3L2.5 ****** 9.5 mm2
4L2.5 ****** 11 mm2
2H2.5 ****** 13 mm2
3H2.5 ****** 14 mm2
4H2.5 ****** 16 mm2
2L4 ****** 11 mm2
2H4 ****** 16 mm2
2H6 ****** 18 mm2
3H6 ****** 20 mm2
2H10 ****** 24mm2
3H10 ****** 27mm2
2H16 ****** 30mm2
3H16 ****** 34mm2
Thanks for that Lenny, may be usefull in the future.We just write 'MICC' or 'sheath', and have never been picked up for it, do you always write the size, or a combination of the two?
thanks Lenny.. I was getting my self a little confused with the pyro being two core, apologies for not replying earlier thanks again Stylus
Reply to r1 r2 testing on micc cable in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thank you very much for the detailed answers! I was really scratching my head with this yesterday then I woke up today and had a crack at it and...
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...