C

captainconduit

hi folks

Carried out all my r1+r2 tests in db and recorded, carried out ze and zs tests.Comparing the results, my r1+r2 are higher than my zs in some circuits, i have read its earth parrallel paths. What results should i record on test sheet as formula zs= (r1+r2) +ze suggests my results are incorrect, can anyone help
 
Record the measured R1R2 and the measured Zs....that is the actual Zs and so it is that which will determine the fault current and the disconnection time when the circuit is energised....not the calculated value.
 
Last edited by a moderator:
(R1+R2)+ZE is a "worst case" since it is the actual ZS of that particular circuit. As long as you record the actual R1+R2 value then you can enter either the measured or calculated ZS.
 
Always recording the calculated values looks suspect and can cause aggrevation on any assessments from the like of the NICEIC.
As ZS values have to be taken with the main earthing conductor connected to the system, it is always expected for the parallel paths to affect the readings, causeing a lower than expected reading.



However... if carrying out the reading would cause you exposure to live parts.. i.e. a fcu or light fitting, then this can conflict with the building regulations and so should be calculated.



My rule of thumb is to measure ZS on sockets, and calculate on light circuits etc.. NICEIC's Tony Cable explains all this in one of thier DVD's and so I always use it and they never have a problem.
 
Last edited:
Always recording the calculated values looks suspect and can cause aggrevation on any assessments from the like of the NICEIC.

If you can either measure ZS or calculate it why on earth would it look suspect and why would it cause aggrevation..
 
Always record what you measure. No one can criticise if you are truthful. If you took your NICEIC assessor around he'd expect to see exactly what you've recorded. It always provides a good talking point aswell. The only reason you can't disconnect bonds, energize circuit and test to get a "clean" result is because of the safety implications. You'd only do it out of interest and once you've reconnected the bonds you could compare. Domestically this is less relative because of the new plastic water mains and gas service pipes. In large commercial and industrial installs it makes a huge difference.
 
Always record what you measure. No one can criticise if you are truthful. If you took your NICEIC assessor around he'd expect to see exactly what you've recorded. It always provides a good talking point aswell.

I quess all assessors think differently then, on a previous commercial unit install we calculated ZS from R1+R2 this provided a good talking point as we recorded the "actual worst case" ZS and as long as you can explain why caculated and measured ZS values will vary then thats all thats needed.

The only reason you can't disconnect bonds, energize circuit and test to get a "clean" result is because of the safety implications. You'd only do it out of interest and once you've reconnected the bonds you could compare.

You would never ever disconnect all bonds and re-energize the circuit to test.

I would fully agree that measuring ZS of a circuit during a PIR is perhaps more acceptable if you cant isolate circuits. However for a new installation there is no reason that recording a calculated result is fraudulant, suspect, or a source of aggrivation.
 
When I design from plans you have to use the standard Ze qouted in the osg. If you then base all circuits on this,any parallel paths are a bonus and you'll never be over max Zs. Based on that you can't be wrong if you add r1 + r2 to Ze from on site measurements. If your measured Zs differs it's fine because we all know why and I can't think of a reason why it would be worse. I actually have a book telling you to disconnect bonds for Zs readings!! My NIC assessor got me to measure Ze with and without bonds ( iso off of course) to show plastic services have no affect on Ze.
 
If you can either measure ZS or calculate it why on earth would it look suspect and why would it cause aggrevation..



Because when I assess guys and realise they've all done calculations, I'm required to ask them to demonstrate obtaining the values by measurment to prove their competance. You'd be surprised how many people don't understand how to carry out live testing. Furthermore it has become apparent some sparks are now predicting these R1&R2 measurments, and using the calculations reason as an excuse for all their readings to be incorrect.
 
Are you saying that people are actually using design figures for their test results? They could fill out the form before the job has begun. Nice!
 
I've seen it done before. I collared a guy working for a London loft conversion company. I was inspecting it for an initial verification and asked the guy to hand me the initial design. He gave me the pack issued from the office, which included all the the test certificates post dated prior to the installation being carried completed.

It was upon having reported this, and finding out that the company were fined and not removed from the enrolment that I decided to stop doing inspections for said company and have since switched to two others.
 
Ah HA, i know who you mean by enrolment. You can't make money from somebody being excluded. We've called in the big guns on a couple of instances and they did nothing! Contractor drives around still badges on van etc. They didn't even get him to fix it all.
 
Well why would they want to remove free advertising. :rolleyes:



My own company is still enrolled under them, till the 20th of this month anyways.
 

Reply to r1+r2 too high in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
281
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
791

Similar threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
996
For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
378

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top