snowplough

hI guys,
Wonder if any of you can clarify the reason why you test at furfest ceiling rose when doing the R1+R2 reading on a lighting circuit as no matter which way i look at it the switch opperating that ceiling rose covers the same distance so why cant you take the reading from that unless of course the line and earth both terminate in the last rose .

Im just starting level 3 so i appreciate your feed back.

snowplough
 
usually lights are wired on loop-in. so your circuit is fron the CU to the last light permanent L/N/E. as that is the furthest point, that is where you measure R1+R2. the switch wire is irrevelant. if wired to switch first, the the switch has to be closede to measure L/E
 
Thanks for your replys guys although im still a little confused , i understand the highest reading should be noted as the R1+R2, and my tutor said it always at the last rose in a healthy circuit ai assume he means, but when i look at the length of wiring ,even though the line does finis in the last ceiling rose , if the earth finishe in the switch the surely the totall lenght of cable i.e R1+R2 is same in the last switch and rose that it feeds so surelly the readings should be the same in an healthy circuit ,so ou can take your R1+R2 from either.

Many thanks

snowplough
 

Reply to R1+r2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K
  • Question
This potential client seems to be making progress in terms of being interested in proper chargers and answering my query questions. I have also...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top