Peter Woodford

Guys,

not done formulas in a very long time and need to get back into it. If I have a Zs 0f 0.48 ohms on a 230v supply how do i work out the R1 + R2 value. if poss can you send me the working outs on how to do this.

thanks in advance
 
If Zs was obtained using a loop impedance tester then it would include parallel paths, and give a lower value than Ze+R1+R2.

I suppose in theory you could loop test at the board with bonding still connected, then deduct Zs from that figure.
This is not what I would do, but just offered it for discussion.

The correct way would be taking the live out the MCB, put it on the earth bar and measuring at the other end of the circuit.
 
You need to know the Ze which will be deducted from the Zs to leave the R1 + R2 value

ZE + (R!+R2) = Zs

You formulas missing the F factor (1.2) for 70 celcuis PVC
if designing the circuit the Zs design = to Ze + F(R1+R2) where Ze is 0.35 TNC-S or 0.8 TN-S and F = 1.2 (pvc conductors table 9C on site guide)

As well if you performing a periodic inspection and are unable to measure Zs the you can measure R1+R2 and then Ze, then finally Calculate the ZS for direct comparison with BS 7671:2008 usind the following formula

Zs calculated = Ze measured + 1.2(R1 +R2 measured) ( this is known as the summation method)

Personelly be told Zs-Ze does not = R1+R2 nor should it ever be used as a short cut to actual testing.

Guys,

not done formulas in a very long time and need to get back into it. If I have a Zs 0f 0.48 ohms on a 230v supply how do i work out the R1 + R2 value. if poss can you send me the working outs on how to do this.

thanks in advance

Peter have a read of GN.3 Appendix B, there are a number of worked examples that may be useful near the back of the book.
 
Last edited by a moderator:

Reply to R1 + r2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
485
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
956
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
900

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
339
Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
918

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top