I have just practised on my circuit at home.
Was doing the ring continuity test and had the following results:
R1 = 0.49
Rn = 0.50
R2 = 0.99
(as per step 1 in the OSG).
As it states the r2 reading should be proportionately higher than that of the line and neutral loops - is the above acceptable?
It is old wiring colour on the ring and the csa of the protective conductor seems only slightly smaller than the line and neutral, which is approx 1.5mm.
OSG states the 1.67 x rule which would indicate in ideal scenario the R2 reading should be approx 0.83.
Any advice would be appreciated.