R2 Calculation | on ElectriciansForums

Discuss R2 Calculation in the UK Electrical Forum area at ElectriciansForums.net

S

Sck

Help with a calculation please?

R2 = (Zs - Ze) x 1000
(L X1.2) - R1

R2 = (3.83-0.4) x 1000
(30 x 1.2 ) - 7.41

= 87.87 mOhms/m

How come i keep coming up with 3401.41??

Next problem

Ze = 0.4 Ohms

Zs = 0.4 ( (7.41 + 18.10) x 30 x 1.2 )
1000
= 1.32 Ohms

How come I come up with 0.93276

Going Stir Crazy here, please help me out on this one guys

Thanks
 
Sorry Scenario is:

4.5 Kw fixed load single phase heater, using 70 degrees thermoplastic cables, running in PVC conduit, over 30metres. Measured Ze is .4 ohms
Iz is 20A using a BS 3036
No correction factor for any thermal insulation needed
Table 4D1a and 4D1B gives me a voltdrop of 10.56v
Using singles I need to determine which size CPC to use

Zs = Ze + (R1 + R2) X 30m x 1.20
1000
= 3.83 which brings me into the question in the first post

Many thanks

D
 
can we have the full question if possible? I've seen a question like this and you need to get your R1+R2 values from table B1 in GN3. If its the same type of question.
Thanks for the reply

Basically I wish to know the size of the CPC to be used for the final circuit, also how I come up with the answer pasted below

R2 =
(Zs - Ze) x 1000
(L X1.2) - R1

R2 =
(3.83-0.4) x 1000
(30 x 1.2 ) - 7.41

= 87.87 mOhms/m

How come i keep coming up with 3401.41??

Next problem

Ze = 0.4 Ohms

Zs = 0.4
( (7.41 + 18.10) x 30 x 1.2 )
1000
= 1.32 Ohms

How come I come up with 0.93276



Many thanks

D


 
once youve worked out your R1+R2 (from the formula in my edited post) you add that to the Ze, This gives you your Zs, (Providing that complies with the max permitted) You then need to work out your fault current,
So 230v/Zs Should give you an answer in Amps.
Then go to your time current graphs for the relevant breaker and find out how long it takes to operate. With this you can work out your csa size. Basically (square root) fault current sqaured X time / Conducor material factor found in tables 54.2-54.6
Thats my understanding, but I could be wrong, and I'm sure someone will be along soon to tell you a definate answer
 
you've got the - R1 bit in the wrong place , it should be subtracted after the division by 1000

so it should read ....

R2 = ( Zs - Ze ) x length x 1.2 - R1

1000


edit ; the 1000 wont centre under the line lol.
 

Reply to R2 Calculation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
900
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
260

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top