M

markthespark

Hello i havent done much testing before so i am trying to brush up on my Testing skills before i join Elecsa, i have a couple of questions about R2 testing please.

I understand how to carry out R1 R2 tests using method 1 and that we do them to calculate the Zs of our circuit Zs=Ze+R1+R2

But i dont understand if we are carrying out an R2 test using a wander lead what sort of maximum values will we be looking for and also how can we calculate the Zs without the R1 reading.

Also out of interest on EICR why is it necessary to do the R1 R2 tests when we can measure the Ze and Zs and calculate the R1 R2 values?

Many thanks in advance.
 
R2 tests with a wander lead will give you the cpc resistance on it's own at each point.a R!+R2 can then be done at the furthest point. to get a Zs value when measuring just R2, you will have to measure it, not calculate. on a EICR, it's permissible to omit R1+R2 readings ( also depends on the limitations of the report ) as long as the Zs readings are within limits.
 
Also out of interest on EICR why is it necessary to do the R1 R2 tests when we can measure the Ze and Zs and calculate the R1 R2 values?

Zs minus Ze is not an accurate way of calculating R1 + R2 because Zs will include any parallel earth paths, R2 proves in theory cpc continuity but again parallels are a bummer, as telectrix says ZS is the important thing on EICR and R +R2 can be ommitted or lim
 

Reply to R2 Testing Help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
940

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
255
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top