sparky1ste

Hi All,Testing high level lights in a factory,on this occasion i did R2 test as i couldnt reach the lights.when recording values how do i record zs values when caculating.
 
Find out the conductor size of the lighting circuit and then you will be able to calculate your zs by using the formula zs=ze[r1+r2] ie if the conductors are the same size then r1will be the same as are r2 if not and eart is smaller the1.7 value comes in refer to gn3
 
Nice low earth path if metal fittings are bolted to bonded structural steel...
Zs would go down as a limitation for me if I couldn't access to test.
 
...if not and eart is smaller the1.7 value comes in refer to gn3

That would be 1.67 and that's only for 2.5/1.5mm² i.e 2.5 ÷ 1.5 = 1.67.

However the OP needs to do things the other way round, if indeed the cpc is smaller than the line. If this is the case take the R2 reading and multiply it by (cpc size ÷ line size). The result will be R1. Add this back to R2 to get R1+R2..

R1+R2 = (R2 x (cpc ÷ line)) + R2
Zs = Ze + ((R1+R2) x 1.2)
 
Last edited by a moderator:
I don't see how you can calculate an R1 or a Zs from an R2 reading that may have parallel earth paths and an R1 which may have poor connections.
limitation is the only way if you can't access for testing.
 
I don't see how you can calculate an R1 or a Zs from an R2 reading that may have parallel earth paths and an R1 which may have poor connections.
limitation is the only way if you can't access for testing.

Agreed. My post was really in response to farm's post about the 1.67 value and how the value of R1 could be calculated from the value of R2 assuming you had no parallel paths etc.
 
Jud just a last one before I retire for the night were did you get r2 divided by the CPc formula from if I'm honest not come across it before not seen it in any books please advise

The 1.67 value comes from the same formula and is for 2.5mm² with a 1.5mm² cpc...

R2 = R1 x (2.5 ÷ 1.5)
R2 = R1 x 1.67

If you had the value of R2 then the part inside the brackets gets reversed...

R1 = R2 x (1.5 ÷ 2.5)
R1 = R2 x 0.6

As another example the formulas for 6mm² with a 2.5mm² cpc would be...

R2 = R1 x (6 ÷ 2.5)
R2 = R1 x 2.4

R1 = R2 x (2.5 ÷ 6)
R1 = R2 x ​0.42

It's just ratios

Small error. It's multiply not divide. Corrected above
 
Last edited by a moderator:

Reply to R2 Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

Similar threads

You would be best checking all connections as it is possible it is having a cumulative effect.
Replies
5
Views
386

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top