Is it possible to use a wander lead when testing a ring ? Doesnt sound right to me but a guy I did a bit with said he does for his r2 on a ring?!
 
tell him to check Guidence Note 3, last time I looked, this method on a ring circuit isn't in print!! Otherwise ask him to demonstrate, and let us know what he's doing.
 
IMO no when testing a ring you also have to test r1 rn & r2 end to end resistances. So having gone to the bother of doing this you then cross connect and take the appropriate R1 + R2 readings. This method also verifies polarity.
 
The only scenarion I can think of would be if the containment system was also used as a CPC. You would use a wander lead and measure R2 from numerous points within the installation, and would hope to achieve a higher reading as you distanced yourself from the origin.
You would measure R1&R2 without the wander lead, but would need it to measure R2 to verify integrity through the system.

I doubt, however, that this is what he is referring to.

R2=Yes
r2=No.
 
Hi,

There is one other time that you could use this method.

If, on a PIR, there are accurate and up-to date records of previous EIC & PIRs, including test results, and there is no evidence of alterations to the 'Ring Final', then it may not be necessary to carry out the 'Continuity of Ring Final Conductors' tests.

If this is the case, there is still a requirement to confirm 'Continuity of CPC' on the ring final circuit.
This you would do with a wander lead from the MET and test at the earth-pin of each socket outlet.:)

You wouldn't be taking readings, by the way........not necessary, you're just confirming continuity.
 
Last edited by a moderator:
ok quized this guy today he says that he disconnects the two legs of cpc and tests from those together to each outlet using a wander lead? Then records that as his R2 reading on his certs??
 

Reply to R2 Wander lead in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

I have a set. I must admit that I seldom use them however. But the concept is good in my opinion.
    • Like
Replies
2
Views
878
  • Question
Yes that was me. If you change your mind give me a shout and I’ll sort something out for you 👍
Replies
5
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top