I would like to ask a question about how Ra links to EFLI, what is the connection?
When you measure Ra properly with a decent earth resistance tester is the reading you get equivalent to R2?
If you had an EFLI tester and you got a value of 100 Ohms would that mean that if you measured the value of R1 and it came out at 1 ohm would that make your Ra value 99 ohms?
Does the Ra value measured using an earth resistance tester substitute the R2 value in your calculations for EFLI?
I am just trying to understand the connection between Ra and R2, Ra being the soil resistance and R2 being the resistance of CPC back to the star point of the transformer.
I'm really trying to get my head round earth rods and Ra values.
Thanks.