did you do an end to end test at the DB to test for a ring?
if it was indeed a ring then the 30a fuse would have been fine.
I kind of fibbed slightly when I said that I was conducting a PIR, I haven't really started it yet.
I was actually asked to add two socket-outlets, one in a bedroom and the other in the kitchen.
The one in the bedroom was to be spured back to back with one in the living room.
When I removed the socket front in the living room, to drill through the wall, I noticed that there was only one cable, so at first thought it was already spured.
I thought that I would have a look at the other socket in the bedroom to see if I could spur from there instead.
After discovering just the one cable at this socket, I decided to check out all the other sockets 9 in total.
Eight sockets have only the one cable, and just the one directly over the CU has two. There is also an old 6mm² feed to an FCU which was for an immersion heater (long since removed) on the same circuit.
I quickly conducted some Zs test at each socket, and found such a disparity of readings that it suggests the sockets are spider rather than on a ring. Readings varied from 0.17
Ω to 0.55
Ω.
I then suggested that I should return to conduct a PIR, which has been agreed.
As I charge a fixed price for a PIR, I didn't want to get the work of the sockets mixed up with the price for the PIR.
So I finished the sockets off, changed the CPD to 20A, and will return tomorrow to conduct the PIR, when I will conduct the tests at the DB, and also take a look at the mess in the loft.
Obviously I won't bother re-testing the Zs at the sockets, as I've already got those results along with the Ze of 0.09Ω and the PFC of 3.77kA (TN-S).