On a radial circuit, do all sockets require duplicate protective conductors back to the cu.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Radial socket circuit - duplicate protective conductors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
this thread is 8 years old. to answer your question, you assume it to be so if you have several computers or other iT gear on the circuit. it's what is known as hi-integrity earthing. if 1 conductor breaks in te socket, you stoill have the other.ok so how would you correctly calculate the likelihood of there being in excess 10ma being carried by the CPC in a domestic setting ?
Hardly a likely scenario Luke, this sort of circuit is more Commercial or industrial rather than domes tic, not saying it couldn't happen, just unlikely.ok so how would you correctly calculate the likelihood of there being in excess 10ma being carried by the CPC in a domestic setting ?
Thanks telec, yes I understand the reason for it but just curious about how you would go about considering if there is likely to be leakage of 10ma along the cpc ? How would you establish (without clamping it) if there would likely be leakage when designing say a 4mm radial socket circuitthis thread is 8 years old. to answer your question, you assume it to be so if you have several computers or other iT gear on the circuit. it's what is known as hi-integrity earthing. if 1 conductor breaks in te socket, you stoill have the other.
how you would go about considering if there is likely to be leakage of 10ma along the cpc
3 items of IT equipment if each produced a leakage current of 3 mA.