S

SW1970

Hi, newbie here. Friend has asked for opinion on quote from another sparky. Single radial to conservatory replacement. Proposal is 6mm2 feed for 4 socket outlets and 6 lighting points back to CU. No mention of RCD or fused units in conservatory. Cable run 20m, floor area 25m2.

I think solution should be separate feeds of 2.5mm2 and 1.5mm2 back to RCD protected MCBs of 20A and 6A. Cable run is straightforward.

Can you guide on whether sparks approach is ok (in particular it all being on one circuit) and if mine is more appropriate?

Many thanks
SW.
 
Guds mornin if theres no probs gettin bac 2 DB then all circuits taken 2 that.If major concern gettin 2 DB then personally i wud --- offa local circuits ie ring/lights cheers ta ra bab
 
Is there a reason he chose 6mm, was he worried about going into insulation which could in certain circumstances derate a cable current carrying capacity (Iz) by 50%.

I've not done a conservatory for several years now but have to admit the favourite method was to spur off a local ring final circuit in a FCU with a 13amp fuse to feed 3 or 4 sockets, and at any of the sockets take another FCU off with a 3amp fuse for the lights. It was mostly done like this to save cost really. Also by doing this you kept disruption to the main house to a minimum.

But every installation is different and perhaps they are going to use larger loads in this one, perhaps a portable AC unit. or some electric heaters, so you would have to judge what is the most cost effective really.

Certainly nothing wrong with your method, it will depend really on loads, disruption to the house etc
 

Reply to Radial to conservatory in the Australia area at ElectriciansForums.net

Similar Threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
637
  • Question
I appreciate your concern for my safety and the law of the land. However I'm not asking anyone here to vouch their advice or be responsible for...
Replies
18
Views
4K
Hi all, I’m new to this forum so please bear with me. I live in a bungalow and would like to repurpose an unused shower cable to supply one new...
Replies
0
Views
4K
  • Question
if the 6mm is clipped direct, it does not, in itself, require RCD protection, so split the tails and fit a 40A MCB in it's own enclosure via...
Replies
12
Views
3K
OK, so as a quick update to this. I found a junction box (Wago Abox SL-2,5/4² # 80680701, see image) that looks like a great fit for my needs...
Replies
3
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks