I doubt that they'll say anything, as they will have no idea what you are on about.
Nice sarcasm!!!!
No seriously an extra returning earth cable from the final socket as per On-site guide
what page is that on, mate
I think you must be reffering to High Integrity Earthing, as used where there are expected to be high earth leakage, I believe 10mA or above.
Only where the earth leakage is expected to be 10mA or above.
If there are two similar Radials, the CPCs can be linked to form a ring.
where there are several pieces of IT equipment plugged in to the circuit e.g. 6 computers.
I generally allow 3.5mA per computer, so 3 or more computers on a circuit and I will install high integrity earthing.
Sorry to be pedantic about this but can someone explain why 10mA flows because of computers and some lighting circuits...You learn something new everyday!
power supplies in pc's. ballasts and control gear in lighting. all have leakage currents due to design.
no but you need a supply of gas mantles.
You can virtually say, any appliance or equipment, with a capacitor on the incoming supply will give a leakage current. Most electronic equipment will have supply filters, to protect the electronics against spikes, noise etc. Computers and other IT stuff will also employ these at a higher level, on the incoming supply. These will generally allow higher than normal leakage currents to flow directly to earth conductor, by the means they are connected between phase and neutral to earth...
Radials - earth return
Talk Electrician Forum
Electricalserv,
Engineer54,