Any of you guys and girls out there work on Rako lighting systems?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Rako lighting systems in the Lighting Forum area at ElectriciansForums.net
Come across them every now and again. Whats the issue, Rako have quite good tech support if you just need some help,
Hi Avo Mk8,Also in each transformer box as well as the fuse appears to be a varistor surge limiter in series with the toroidal transformer, which is there to reduce the inductive surge. I don't believe they are prone to fail short-circuit, but that might explain the tripping and fuse blowing. Rako could maybe confirm if this is a known problem, and supply replacement parts?
I don't see any residual current breakers, only MCB's.
Yes. Correct re the MCBs blowing and it being a sub-board off the main RCD unit. The lamps are 12v retrofit MR11s and hence need the transformer (one per circuit each with around 9 lamps), there were halogens previous and hence the transformer is a bit over-clubbed for the LEDs. There is one WML-300 dimming unit per transformer. Yes I am planning to change the drivers for something more modern - but there seems to be Rako-phobia amongst the local sparkies - do you do jobs in London? I renamed the project file as a jpg as otherwise I can't upload here - hopefully that works.As AVO mentioned, there is not an RCD in the fusebox you have photographed , this looks like a sub board off your main fuseboard ? where there may be an RCD, if it is the B10 MCBs that are tripping this makes sense if the fuse is also blowing, however i am confused about the role of these transformers , are they remote from the Rako kit as it looks like the actual lights are commoned together on the output of the transformers.
Dont suppose you have the Rako project file to hand ?
What i would have expected is that each lighting zone is connected to an output directly of the Rak dimming unit. So do these transformers work for just 2 zones, if so, and the lamps are LED , i would be looking at removing them and installing the appropriate dimming LED driver to replace these transformers.
Again a call to Rako will confirm whether these transformers are appropriate for this installation. I suspect not
You are correct, it is the MCB that is tripping - there is an RCD upstream, but this seems to be fine.As AVO mentioned, there is not an RCD in the fusebox you have photographed , this looks like a sub board off your main fuseboard ? where there may be an RCD, if it is the B10 MCBs that are tripping this makes sense if the fuse is also blowing, however i am confused about the role of these transformers , are they remote from the Rako kit as it looks like the actual lights are commoned together on the output of the transformers.
Dont suppose you have the Rako project file to hand ?
What i would have expected is that each lighting zone is connected to an output directly of the Rak dimming unit. So do these transformers work for just 2 zones, if so, and the lamps are LED , i would be looking at removing them and installing the appropriate dimming LED driver to replace these transformers.
Again a call to Rako will confirm whether these transformers are appropriate for this installation. I suspect not