Give me a leakage clamp meter every time, over a MFT ramp test. Far too many variables regarding the accuracy of a ramp test. It's only been relevantly recently, that MFT's ramped up in 1mA steps, on earlier models, it could be anything between 3 to 5mA steps, not exactly very beneficial when fault finding.

Not sure why anyone would find it remotely necessary to ramp test an RCD device after it had passed all it's standard obligatory tests eg X 0.5, X1, X5, ...seems a pointless exercise to me!!
 
Yes as Richard points out and I touched on too your looking to comply with a trip 'time' when your meter give out 0.5, 1, and x5 rated tripping current. The ramp test is for diagnostic purposes and subject to many factors like existing leakage etc... but dropping all the load off would not have decreased this value as any mA leakage on appliances would be an addition to the result on your meter.

Tripping occurs at 24mA on ramp with loads connected
Tripping occurs at 20mA on ramp without loads connected therefore background leakage due to appliances is 4mA


Im confused why your expressing a value that is not part of the test procedure, if you pass the .5/1/x5 test then the meter has created the correct leakage and the trip times are shown.

is it not the other way round?
 

Reply to Ramp test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
545
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

If it’s rcbo’s, then it’s 30mA per circuit… an rcd mainswitch is 30mA for ALL circuits It may just be a cumulative earth leakage which was just...
Replies
9
Views
712
You would be best checking all connections as it is possible it is having a cumulative effect.
Replies
5
Views
486

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top