I am an adult learner. I understand the theory behind the 30mA trip rating (for example) of an RCD but I need some help understanding what the 63A rating (for example) actually means. My understanding is that RCD's do not provide over current protection, that would be provided by MCBs (for example) downstream of the RCD. Am I correct in saying that the 63A rating (for example) is the "switching" rating of the device rather than the current carrying capacity of the device? Any advice would be appreciated.
 
It is the maximum continuous current that can be passed through it.

it will be capable of disconnecting under full load but will not provide any over current protection
 
It is the maximum continuous current that can be passed through it.

it will be capable of disconnecting under full load but will not provide any over current protection
Thank you for your prompt reply. I watched a video from a well respected YouTube electrician (bigclive.com) and he was tearing down an RCD that was sent in by an electrician to see whether overload was the cause of failure. (View: https://www.youtube.com/watch?v=9wcPw5hUNpQ
) and he shows a picture of the CU that it was removed from. He also says that "..the 63A isn't a tripping current, it's the current it can handle on a continuous basis" (As you say above). I attach an image from the video and can't understand what an electrician would set up a CU with such high loads all (on a split board) 1 RCD. Any thoughts would be appreciated[ElectriciansForums.net] Rating of RCD's
 

Reply to Rating of RCD's in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
875
If the main DB RCBO is there to provide additional protection (as it most probably is), then no, as S type RCDs are not suitable for providing...
Replies
1
Views
1K
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top