The bit where I cut to the chase is in bold below if you can't be bothered with the back story.
Changing MCB in main house DB for garage supply, so turned off at main switch.
Contactum metal DB (about 4 years old), 2x MCBs for existing feeds to sub boards, the rest RCBOs (full height, single pole, type AC). TN-C-S, bonding good.
On turning the main switch back on, one of the RCBOs tripped, and would not reset. Kitchen sockets.
Kitchen re-done 5 years ago, new cables all the way back to the board. Ring continuity fine, N-E fault of <1Ω (measured at DB). Not MΩ, not even kΩ: Ω.
Traced to between 2 sockets: local R1+R2 between the two sockets = 0.15Ω; N-E = 0.09Ω from one, 0.06Ω from the other. So, dead short, 3/5 of the cable length between the two. Exact location and cause TBC as I forgot my X-ray specs and this is not a can of worms I wanted to open on a Friday.
RCBO (with circuit disconnected) tests out fine.
Question is... how was the circuit ever working with that fault there? And, am I right in thinking that if there had been a power cut since the fault occurred, it would have tripped then (and not been able to be reset)? Is there a way that a dead short, N-E, can "blind" an RCBO (in the same way flooding it with DC can)?
Was really, really annoying, especially on POETS day. All I did was turn the power off then on again, the fault makes itself apparent, and I have to deal with it. Client was understanding, particularly when shown fault readings and after explaining everything, but just as confused as I am about why it was working at all.
Changing MCB in main house DB for garage supply, so turned off at main switch.
Contactum metal DB (about 4 years old), 2x MCBs for existing feeds to sub boards, the rest RCBOs (full height, single pole, type AC). TN-C-S, bonding good.
On turning the main switch back on, one of the RCBOs tripped, and would not reset. Kitchen sockets.
Kitchen re-done 5 years ago, new cables all the way back to the board. Ring continuity fine, N-E fault of <1Ω (measured at DB). Not MΩ, not even kΩ: Ω.
Traced to between 2 sockets: local R1+R2 between the two sockets = 0.15Ω; N-E = 0.09Ω from one, 0.06Ω from the other. So, dead short, 3/5 of the cable length between the two. Exact location and cause TBC as I forgot my X-ray specs and this is not a can of worms I wanted to open on a Friday.
RCBO (with circuit disconnected) tests out fine.
Question is... how was the circuit ever working with that fault there? And, am I right in thinking that if there had been a power cut since the fault occurred, it would have tripped then (and not been able to be reset)? Is there a way that a dead short, N-E, can "blind" an RCBO (in the same way flooding it with DC can)?
Was really, really annoying, especially on POETS day. All I did was turn the power off then on again, the fault makes itself apparent, and I have to deal with it. Client was understanding, particularly when shown fault readings and after explaining everything, but just as confused as I am about why it was working at all.