RCBO fly leads | on ElectriciansForums
Discuss RCBO fly leads in the UK Electrical Forum area at ElectriciansForums.net
Heres a debate for you, seeing as this place is as dead as a doornail today.
I have been testing a street of domestic properties recently, wired in 2008 with all rcbo's. In some properties the electrician has put all the white fly-leads into one terminal in the earth bar, In the others they have put each one in with the respective circuits cpc.
Which way do you do it?
I'll start the ball rolling by saying I would put them all into the same terminal (for domestic anyways) for the following reasons
a) When you come to doing an EICR, you only have to undo one connection to test the circuits using method 2 rather then disturb every single earth connection.
b) its a lot bl***y easier to install.
When it comes to commercial where there may be only 1 or 2 rcbo's in a TPN board then I would put them with their respective cpc.
Opinions?
As a side question: do you sleeve the white flylead in green/yellow? Most I've seen (admittedly not thousands) are sleeved, but according to the 'official' colours, cream is the colour of 'functional earth' not G/Y.
Don't sleeve them, They would be green/yellow if they were meant to be, as you rightly say, cream is the colour for a functional earth.
both in same terminal.
if your CU has the facility to provide 2 earth terminals for each circuit , then i would reserve the use of the second terminal for high integrity earthed circuits that require a seperate connection for both protective conductors.
if your CU has the facility to provide 2 earth terminals for each circuit , then i would reserve the use of the second terminal for high integrity earthed circuits that require a seperate connection for each protective conductor.
I used to always do it that way biff but after testing a lot of houses, it makes it a right B***ard to megger, you have to disturb the cpc of every circuit to remove the flylead. From now on I am putting all the cream coloured leads into a group and into one terminal of the earth bar as it makes doing insulation resistance an easy job.
Either way its completely inconsequential, i'm just debating for the sake of it really
I like the term 'bungled', makes me sound like a right bodging *** lol. I just think it makes sense when thinking of future EICR's on properites although it may sound a bit rough
Doesn't really matter does it - can and is done either way.
Just over time and with several other electricians in things get tangled ... if everything seperate, should you ever have to replace the RCBO then it is usually easier to figure out which fly-lead is which when they're seperate.
That's the only reason i try put them in there corresponding earth terminals.
I always strip approx 100mm of the insulation off the fly lead and then obviously twist it together nice and tight with the cpc......as it should be done!!!!! :)
Seriously though I usually put fly lead with the respective cpc
Reply to RCBO fly leads in the UK Electrical Forum area at ElectriciansForums.net
Yup will do exactly that when I'm back down there. Thanks for the help
And exciting when that Hager AFDD finally tripped 😂
nicebutdim
N
