Hi, I am looking at a lighting circuit, Hall, Bedroom, Bathroom which is on an RCBO 6amp, the lighting circuit is not working, the RCBO has NOT tripped. I have done a quick test with a voltage stick just to see if there is power to the switches - and there is. Would I be right in thinking this could be a neutral fault ? but I am confused as to why the RCBO has not detected this.

thanks, Ian.
 
Why don't you test at the first light that isn't working in the loop and see if you have voltages between line and earth and line and neutral, might be a lose neutral in the last light that is working or first light that isn't! Would not definitely trip rcd as if it isn't in contact with cpc or live so the rcd won't see the fault. Hope this helps I'm on my phone so might be a bit gibberish
 
Sounds like a dis. neutral, check the board then work your way through the circuit but as it affecting all the lights it's more likely to be at the first one. Check the N-E should be 0V but if it's disconected you will have a voltage on the neutral assuming the cpc is present and connected
 
Last edited:
thanks to all who replied. I found the issue. I made my way around the circuit doing continuity tests between the fittings and switches and the RCBO neutral and the switches and low and behold the first point in the circuit where the line and neutral were looped behind a switch there was a little neutral fellow all on his own waiting to get connected.
 

Reply to RCBO NOT TRIPPIN! - Lighting circuit not working in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! âš¡ Please note that all EV Chargers and...
Replies
0
Views
228
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
Hi All, Looking for some advice into my build. What I've basically done is add additional RCD protection to my 100% off-grid 12V 3300W Inverter...
Replies
0
Views
194

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top