I'm stuck here fellas.
I have a radial with only one double socket outlet in 2.5mm T&E on a 20A RCBO running five meters in surface mounted trunking. TN-S, R1 and R2 good, 243V measured, Ze 0.12, Zdb 0.29, Zs 0.36, IR all +200MOhms.
RCD trip tests all ok at 0 and 180 and ramp 24mA.
Now these sockets are only used for one thing, two 580W water distillers.
Both have been clamped during operation and are drawing 2.4-2.6A as expected.
Both have been IR tested L-E & N-E and +200MOhms.
I am stumped to the point where I may run in a new socket on a new RCBO, cost not an issue the customer just wants it stopped.
My concern is the issue could be with one or both the distillers units and not the circuit.
I don't have a low current clamp meter so cannot measure earth leakage directly.
Any ideas where to look next, I'm still on the job by the way.