I'm stuck here fellas.

I have a radial with only one double socket outlet in 2.5mm T&E on a 20A RCBO running five meters in surface mounted trunking. TN-S, R1 and R2 good, 243V measured, Ze 0.12, Zdb 0.29, Zs 0.36, IR all +200MOhms.

RCD trip tests all ok at 0 and 180 and ramp 24mA.

Now these sockets are only used for one thing, two 580W water distillers.

Both have been clamped during operation and are drawing 2.4-2.6A as expected.

Both have been IR tested L-E & N-E and +200MOhms.

I am stumped to the point where I may run in a new socket on a new RCBO, cost not an issue the customer just wants it stopped.

My concern is the issue could be with one or both the distillers units and not the circuit.

I don't have a low current clamp meter so cannot measure earth leakage directly.

Any ideas where to look next, I'm still on the job by the way.
 
First thoughts are towards faulty distillers..
Have you tried plugging in other appliances?
I'm leaning that way too but cannot think of any definitive way of proving it.

I think it's happening when there thermal overload kicks in, i.e. when they're run dry as they often trip overnight.

I don't want to test that as it may damage the kit but it's the only theory I have at the moment.

I think the customer knows this as they have had them put on a dedicated circuit so as not to take down other areas.
 
Defiantly points to a faulty appliance. A PAT wouldn't necessarily pick this up though, the equipment is likely 'safe' to pass PAT. Could be worth contacting the appliance manufacture.
 
Most likely faulty appliance. How often is it tripping, instantly or randomly? Seen something like this before even though it recently "passed" all its PAT tests. As above swap rcbo for mcb and replace socket for T earth and mark up.

Defiantly points to a faulty appliance. A PAT wouldn't necessarily pick this up though, the equipment is likely 'safe' to pass PAT. Could be worth contacting the appliance manufacture.

Just passed PAT test..:D
 

Reply to RCBO socket circuit tripping. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
753

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
980
  • Question
Im not as clever as you guys. I would be doing what somw others have said, I would be leaving certain items switched off for a period of time...
2
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top