I have come across a couple of Eaton RCBOs in Memera 2000AD boards and they don’t trip at the board when tested but do at the point of use/load, what’s up with that then?
Cheers
 
It needs a load through the sensing coil from the line terminal as the imbalance is detected where the conductor passes through the tunnel to the terminal. Testing direct to the terminals bypasses this. Get an extension socket with the three wires and connect into the rcbo if you want to test at the board.
 
It needs a load through the sensing coil from the line terminal as the imbalance is detected where the conductor passes through the tunnel to the terminal. Testing direct to the terminals bypasses this. Get an extension socket with the three wires and connect into the rcbo if you want to test at the board.
Thank you Westward10. Is it peculiar to this brand?
 
It needs a load through the sensing coil from the line terminal as the imbalance is detected where the conductor passes through the tunnel to the terminal. Testing direct to the terminals bypasses this. Get an extension socket with the three wires and connect into the rcbo if you want to test at the board.
Thank you for that. Is it peculiar to just this brand or a certain age of RCBO?
 
Thank you for that. Is it peculiar to just this brand or a certain age of RCBO?
As far as I know it is just those retrofit rcd pods from Memshield 2. The pod fits a standard mcb but you can also find them in Memera 2000 as they are a similar device.
 

Reply to RCBO testing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

If it’s rcbo’s, then it’s 30mA per circuit… an rcd mainswitch is 30mA for ALL circuits It may just be a cumulative earth leakage which was just...
Replies
9
Views
604
Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
387

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top