Heres a good one for you,
17th ed CU with rcbo's one of wich intermittantly trips, on inspection shows no fault and works fine how do we tell what kind of fault caused it to trip (to give us a clue where to start looking) , ie; was it a short and the mcb/ current rating side of it tripped or was it a earth fault and the rcd side of it caused tripping ( does this make sence so far),
I feel this is going to become more of a common problem ( or am i missing something obvious)

Your thoughts please chaps. (and chapesses)
 
i woluld change it for a nomal mcb and see if that trips if not then we are looking at live to earth fault, if does live to neutral , or just get the megger out andtest the circuit if it test ok test what ever is used on the circuit , could be a faulty appliance.
 
Heres a good one for you,
17th ed CU with rcbo's one of wich intermittantly trips, on inspection shows no fault and works fine how do we tell what kind of fault caused it to trip (to give us a clue where to start looking) , ie; was it a short and the mcb/ current rating side of it tripped or was it a earth fault and the rcd side of it caused tripping ( does this make sence so far),
I feel this is going to become more of a common problem ( or am i missing something obvious)

Your thoughts please chaps. (and chapesses)

You haven't said what circuit it is or RCBO rating?
Checked connections?
Have you checked for a short circuit?
Checked the loading of the circuit?
Unplugged equipment still trips?
Any fridges ,washing machines on the circuit?

If all worked on initial inspection then it would appear if you have covered all other angles that it is something being plugged in or kicking in to cause the trip?
 
FOUND IT!
cable caught by screw tip - just, (i love joiners)
good tip though, if you turn rcbo on with a live fault it turns off with a pop, with an earth leakage fault there is slight delay and it turns off with only a small click.

as an afterthought i suppose you could try and measure for any imbalance with a clamp ammeter???
 

Reply to RCBO testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
227
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
638

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
323

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top