had a job today ,fitted a new board including 5 rcbo's.newlec own brand which is wylex.All rcbo's tested fine apart from the ring circuit 32 amp one.Tripped within the time on 1xIn on both occasions tripped at a time greater than 40ms and then would not trip on the final test.changed the rcbo for a new one still got same result.Anybody got any idea what could be causing this.I did a pir first so all readings ok.loop impedance fine ,ring continuity fine.
 
Testing at various points on ring .quite a few loads still plugged in but not switched on.

You might still have capacitors in circuit or even capacitive coupling affecting the tester display time.

This is why you should test at the terminals of the device with all load disconnected.
 
Hi Guys

When I recently tried testing at the terminals of a RCBO the terminal screw was so far back and hole too small I had to test at socket outlet.
T&E
 
Hi Guys

When I recently tried testing at the terminals of a RCBO the terminal screw was so far back and hole too small I had to test at socket outlet.
T&E

I used to have an old neon driver that somehow all the insulation fell off of it one day, which fitted nicely into the RCBO and then somehow a croc clip attached itself to the driver and I accidentley pushed the test button and it worked, of course I threw the driver away as it was against all H & S issues, but it was handy for that one time I used it:cowboy::angel_smile:
 
I used to have an old neon driver that somehow all the insulation fell off of it one day, which fitted nicely into the RCBO and then somehow a croc clip attached itself to the driver and I accidentley pushed the test button and it worked, of course I threw the driver away as it was against all H & S issues, but it was handy for that one time I used it:cowboy::angel_smile:

Its funny how these dangerous practices can become known to many people after a few years of performing,heaven forbid we should do these sort of things
[ElectriciansForums.net] rcbo testing
 
Hi!
I've never really been clear on how to conduct RCBO tests at the CU. Would anyone be able to give me a quick step-by-step guide? I've searched everywhere but can't seem to find this information. Thanks
 
Hi!
I've never really been clear on how to conduct RCBO tests at the CU. Would anyone be able to give me a quick step-by-step guide? I've searched everywhere but can't seem to find this information. Thanks

You just have 1 probe on the line terminal of the load side of the RCBO and the other probe on the earth bar/terminal with all load disconnected.

Check out Guidance Note 3 page 56 for reference.
 
My Megga multi function tester came with a fancy big red probe with various tips that had never gotten any use as the croc clip leads did the job just fine, then these RCBOs came along and I found the big red probe ideal for getting to the live terminal nice and safely.
 
My Megga multi function tester came with a fancy big red probe with various tips that had never gotten any use as the croc clip leads did the job just fine, then these RCBOs came along and I found the big red probe ideal for getting to the live terminal nice and safely.

Doh! I'd totally forgotten about those. Cheers :)

At my last assessment I asked my assessor if he wanted to see me working with the caps on my probes - so only 4mm tips. He asked if I considered myself competent, I said yes, he told me to get on with it then! (Names and content has been changed to protect the innocent).
 

Reply to rcbo testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

Similar threads

  • Question
It might be worth asking the customer to turn the oven on 45min before you arrive. then do an IR test on the oven from the isolator with the oven...
Replies
6
Views
1K
  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top