Hi guys,
am I missing something obvious? Hager 40amp type B RCBO supplying a 9kw shower (actually pulling 36 amps). Whilst shower is on, no matter for how long/short, everything is ok. However after it is switched off the RCBO trips - this is not immediately, it can happen an hour or two, or even longer after. Cable insulation tests fine, all connections (shower, switch, board) good, Zs fine. Only the shower on the circuit. RCBO ramps at 27ma.
I appreciate that the rating of the RCBO is technically too low and a 45 amp would be better, but I can't see this being an overload issue given when the tripping occurs.
As I started, what if anything am I missing?
Regards.
am I missing something obvious? Hager 40amp type B RCBO supplying a 9kw shower (actually pulling 36 amps). Whilst shower is on, no matter for how long/short, everything is ok. However after it is switched off the RCBO trips - this is not immediately, it can happen an hour or two, or even longer after. Cable insulation tests fine, all connections (shower, switch, board) good, Zs fine. Only the shower on the circuit. RCBO ramps at 27ma.